Absolutely: many electric motors ARE a true 220/240v and KNOT split to operate two seperate needs of the same appliance. They still use both poles to balance the load.
Both new dryers and ranges use the new 4 wire plugs and receptacles. In my house, two of the wires are "hot", a third wire goes to the ground bar and the fourth goes to the neutral bar. In other words, the ground wire and the neutral wire service both "hots". If that is knot what is actually going on, please advise. :)
Terminology again! The ground conductor(green when colored) serves to provide a path to "ground" in the event of a fault(short/leakage) to the external surface of the appliance(which would pose a hazard to anyone touching the appliance). The ground wire maintains the external surface of the appliance at 'ground' potental. The ground conductor is knot intended to serve any other purpose and should NEVER be conducting any current EXCEPT fault current. It is connected, but just sits there doing nothing until a fault occurs.
The neutral conductor(white when colored) serves to conduct any current due to 115v loads. Thus the neutral ONLY serves to conduct this imbalance in currents between the two 230v conductors. If two EQUAL 115v loads were on each of the 230V conductors, there would be NO current in the neutral.
Since the purpose of the breaker is to protect the wiring, an excessive current in ONE pole will cause the breaker to trip. Since this can cause an unexpected condition in any appliance connected, the second pole is simultaneously tripped(mechanically connected).
Not sure how this is helping putttn with his motor problem, but perhaps we are all learning something here.:)
Both new dryers and ranges use the new 4 wire plugs and receptacles. In my house, two of the wires are "hot", a third wire goes to the ground bar and the fourth goes to the neutral bar. In other words, the ground wire and the neutral wire service both "hots". If that is knot what is actually going on, please advise. :)
Terminology again! The ground conductor(green when colored) serves to provide a path to "ground" in the event of a fault(short/leakage) to the external surface of the appliance(which would pose a hazard to anyone touching the appliance). The ground wire maintains the external surface of the appliance at 'ground' potental. The ground conductor is knot intended to serve any other purpose and should NEVER be conducting any current EXCEPT fault current. It is connected, but just sits there doing nothing until a fault occurs.
The neutral conductor(white when colored) serves to conduct any current due to 115v loads. Thus the neutral ONLY serves to conduct this imbalance in currents between the two 230v conductors. If two EQUAL 115v loads were on each of the 230V conductors, there would be NO current in the neutral.
Since the purpose of the breaker is to protect the wiring, an excessive current in ONE pole will cause the breaker to trip. Since this can cause an unexpected condition in any appliance connected, the second pole is simultaneously tripped(mechanically connected).
Not sure how this is helping putttn with his motor problem, but perhaps we are all learning something here.:)